    May I connect # 10 wire to #12 wire
    May I connect # 10 wire to #12 wire
  • Jul 15, 2010, 02:22 PM
    jlyons34

    As long as you are not pulling more than 20 amps
  • Jul 15, 2010, 02:23 PM
    twinkiedooter

    What are you trying to hook up? Or what are you trying to repair. What voltage, amps, etc.
  • Jul 15, 2010, 06:43 PM
    Missouri Bound

    Although the NEC doesn't address it specifically, it's a bad idea to mix wire sizes in a circuit. It allows for the possible overload of the smaller wire by mistakenly fusing the circuit for the larger wire.
  • Jul 15, 2010, 06:48 PM
    stanfortyman
    Quote:

    Originally Posted by Paul4 View Post
    may I connect # 10 wire to #12 wire

    May I ask why you would need to?


    Missouri's reply is completely accurate and correct BTW.
  • Jul 16, 2010, 05:55 AM
    Stratmando

    Only reason I would do something like that is if I had a receptacle on the side of the house fed by #12's, and I wanted to run a Line from there with some distance, then I might use #10 to reduce the Voltage Drop.