Wire UF wire to run to new 100 amp service panel?
My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is 125 feet between boxes. My question is what size uf wire to run? I have heard anywhere from #4-3 with ground, #2-3 with ground or the same but ground at the box on the building??
thanks for any help
Comment on Missouri Bound's post
Does your four wires include the ground? Are you suggesting the following? From the 200 amp panel, run two hots and 1 neutral #4 wires to the shop and then at the shop run a ground #6 ground wire to a ground bar next to the buiding. Do not use the