Lennox condensing unit mod# HS29-030-1P
Great service, here, at askmehelpdesk/heating & ac. Been reading up on past Q&A, and have performed basic TS on my 9 yr-old Lennox condensing unit (mod# HS29-030-1P). When it failed a few days ago, the first thing I noticed was the rusty dual-run cap (C12). It showed no "bowing", but I could feel the internal structure was wobbling inside the case. The schematic on the panel (and other documents) does not show the value of C12, so I phoned Lennox. Unfortunately, their technicians couldn't be bothered to answer my simple inquiry as to the correct value of the dual-run cap. So, I phoned a local commercial electrical contractor that I found in the yellow pages. They directed me to Grainger Industrial Supply. I phoned Grainger, and got the correct value (35+5uf370VAC) for the cap. I registered at their website, logged on and ordered it. It arrived two days later. I installed it, but that was too easy. The unit still wouldn't kick ON.
The 1st time I took readings - low-voltage (26v) was present at the contactor with the unit
powered ON, and the coil activated properly. High-voltage (241.7v) was present at the
contactor (L1 across L2) with the unit powered ON or OFF. There was no low voltage present at the contactor with the unit powered OFF.
I like to be thorough, so I took readings 5-6 min later to verify.
The 2d time I took readings - again, low-voltage (27.1v) was present at the contactor with
the unit powered ON, and the coil activated properly. High-voltage (243v) was present at the contactor (L1 across L2) with the unit powered ON or OFF. Again, there was no low voltage present at the contactor with the unit powered OFF.
Readings on the dual-run cap, with the unit powered ON, were as follows:
C - gnd = 122.4v
H - gnd = 122.2v
F - gnd = 122.1v
Still, NOTHING. Just for the heck of it, I started some random measurements with the unit powered ON. As soon as I measured from H-C12 (wired to S-B1 compressor) to the T1 lead on the contactor (wired to C-B1 compressor) the unit kicked ON. Done and DONE. Must be kind of like shorting out the starter on a car in order to fire a stuck solenoid. Who knew?
Looks like my problem is solved--based largely on previous posts/replies from hvac1000. The unit has been running fine for the past few hours.
Can someone verify that I've installed the correct value (35+5uf 370VAC) dual-run
capacitor?
Hope this post will encourage/help others. Thanks to ALL for the good info; special thanks to hvac1000.