I am install a 400 amp 480 volt panel outside a building. It will be fed from a breaker inside. Can this panel be a MLO or does it have to have a main breaker or disconnect.
![]() |
I am install a 400 amp 480 volt panel outside a building. It will be fed from a breaker inside. Can this panel be a MLO or does it have to have a main breaker or disconnect.
Does not need to have a main, may be helpful for the local operation, but, as long as the main can be locked off, no problem.
It will need to be at least rain tight.