    deananderson
    Kenmore two stages problems
    Kenmore furnace two stages
    M/N : C9MPT07514A3
    G/V smart valve 9541

    Call for heat there , the furnace kicks on however the inducer goes off half way that means when it is going to light up the HSI .
    Checked out the board that is OK
    Checked out the inducer is OK
    Checked out the blower fan that is OK
    P/S closed and shows 24vac on airflow C and NO

    Any comments will be appreciated
  • Jun 12, 2010, 06:36 PM
    deananderson
    Kenmore two stages
    M/N :C9MPT100J16B1
    G/V smart valve SV9541

    Replaced the smart valve and now come across a big problem:

    Call for heat is there , the furnace is humming however the inducer does not get energized . Waited for more than 5 minutes and no go at all.
    The inducer found to be OK
    The blower OK
    The board was replaced with a new one and the problem still there .

    Any comments will be highly appreciated .
  • Jun 12, 2010, 07:12 PM
    Joshdta

    Must be a limit or rollout. Pressure switch
  • Jun 12, 2010, 07:13 PM
    Joshdta

    The only thing that would stop the vent motor is a limit, or loss of heat call
  • Jun 12, 2010, 07:22 PM
    deananderson
    Quote:

    Originally Posted by Joshdta View Post
    The only thing that would stop the vent motor is a limit, or loss of heat call

    You absolutely right however there is no limit on the way but three rollout arount the burner box which are all OK and no problems .
    Tks for quick answer again .
  • Jun 12, 2010, 07:34 PM
    Joshdta

    Does the control board give a fault?
  • Jun 12, 2010, 07:52 PM
    deananderson
    Quote:

    Originally Posted by Joshdta View Post
    does the control board give a fault??

    No not at all . There is no led on the control board . However I replaced it with a new one and the problem still there .
  • Jun 12, 2010, 07:54 PM
    deananderson
    Quote:

    Originally Posted by Joshdta View Post
    must be a limit or rollout. pressure switch

    I put in a new pressure switch and still the problem there . Tks for quick answer
  • Jun 12, 2010, 08:28 PM
    KISS

    <threads merged>
  • Jun 13, 2010, 12:39 PM
    Angrycustomer
    Quote:

    Originally Posted by deananderson View Post
    I put in a new pressure switch and still the problem there . tks for quick answer

    =
    remove the draft motor and the tube to the P/S. make sure its free from moisture and shake the draft motor to be sure there is no water collecting in it.
  • Jun 13, 2010, 09:55 PM
    deananderson
    Quote:

    Originally Posted by rapedcustomer View Post
    =
    remove the draft motor and the tube to the P/S. make sure its free from moisture and shake the draft motor to be sure there is no water collecting in it.

    Tks for the answer . I have already done that and put the motor on test , it is working fine . Tks agn