Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Trane baystat 239 to honeywell th3210d1004 (https://www.askmehelpdesk.com/showthread.php?t=473441)

  • May 25, 2010, 04:24 PM
    dkelly1739
    trane baystat 239 to honeywell th3210d1004
    I am replacing a Trane Baystat 239 thermostat with a Honeywell TH3210D1004 thermostat. The Trane thermostat is wired is follows:

    Terminal Color of Wire

    X2 Black
    O Orange
    G Green
    Y Yellow
    T Tan
    R Red
    W White - W is also jumpered to terminal U
    F Not Used
    B Blue


    The wiring terminals on the Honeywell are as follows:

    Terminal Description

    C 24V Common
    B Changeover valve energized in heating
    R 24 VAC Power
    L Sends output when set to emergency heat
    O Changeover valve energized in cooling
    G Fan Relay
    Y Compressor Contactor
    Aux Auxiliary Heat Relay
    E Emergency Heat Relay

    Can someone tell me which color wires to connect to each of the Honeywell terminals.

    Thanks - Dennis Kelly - Savannah, Georgia
  • May 25, 2010, 06:21 PM
    Joshdta

    c=blue
    y=yellow
    r=red
    g=green
    L=black
    o=orange
    aux=white
    e=tan, jumped to aux

  • All times are GMT -7. The time now is 11:21 AM.