-   -   Is it safe to run #10 wire 25 feet to a 30 amp air conditioner/heating unit (https://www.askmehelpdesk.com/showthread.php?t=472321)

  • May 21, 2010, 03:14 PM
    stan_81433
    Is it safe to run #10 wire 25 feet to a 30 amp air conditioner/heating unit
    Want to run #10 gauge wire 25 feet to a large window unit that heats and cools. Is the distance too far for #10 wire.
  • May 21, 2010, 03:16 PM
    hkstroud

    Yes.
  • May 21, 2010, 04:49 PM
    stanfortyman

    Well the question is not clear.

    A) Does the unit require a 30A circuit?
    B) Or does the unit draw 30A?

    If A), then 25 feet is not at all too far.
    If B), then #10 is not large enough, you need #8.

    The bottom line is what does the rating plate on the unit state as far as minimum circuit ampacity and maximum fuse or breaker?