  • May 15, 2010, 03:12 PM
    rottenrichard00
    55 amps #8 wire run 50 feet
    If you touch a wire and it is hot, is that bad ?
  • May 15, 2010, 03:33 PM
    rottenrichard00
    Should the wires in my house be hot to the touch
    If you touch a houseing wire and it is really hot is this bad ?
  • May 15, 2010, 03:34 PM
    Fr_Chuck

    Yes, it is bad. I would cut the power to those wires till you have it inspected
  • May 15, 2010, 03:39 PM
    rottenrichard00
    Quote:

    Originally Posted by Fr_Chuck View Post
    yes, it is bad. I would cut the power to those wires till you have it inspected

    The main feed wires to my pannel are hot to the touch ?
    How hot can they be ? Should they be cold
  • May 15, 2010, 04:24 PM
    Stratmando

    If that is on a 40 Amp breaker, it will likely trip.
    What size Breaker and what is your Load. Motors, Welders, pumps?
  • May 15, 2010, 04:31 PM
    Stratmando

    A loose connection will generate heat, maybe shutdown power, tighten connections then restore power, an Electrician should do this.
  • May 15, 2010, 05:00 PM
    rottenrichard00
    Quote:

    Originally Posted by Stratmando View Post
    A loose connection will generate heat, maybe shutdown power, tighten connections then restore power, an Electrician should do this.

    I am running a lot of things 4 A/C's ,refer, hot water heater, lights,
  • May 15, 2010, 05:02 PM
    rottenrichard00
    Quote:

    Originally Posted by rottenrichard00 View Post
    I am running a lot of things 4 A/C's ,refer, hot water heater, lights,

    When I turn off some things the wires cool down
  • May 15, 2010, 05:25 PM
    Fr_Chuck

    Wire gets hot if and when something is not right, perhaps they are over loaded and you need larger leads to the panel. Or they have bad or loose connections. You need a professional to check it out, and yes it can be a danger
  • May 15, 2010, 05:41 PM
    rottenrichard00
    I need 100 Amps at 50ft using 8/3 stranded should be cool ?
    I have 8/3 on a 50ft run, I am using 100amps, 50 on each side and my wires are a little warm. What do you think, it would be really hard to replace the wire, The last 3 feet at the panel I cannot get to, if I spliced/ sodered a #6 wire and ran it back 47 feet would that help, remember I cannot get to that last 3 foot piece at the panel. Thanks
  • May 15, 2010, 06:23 PM
    hkstroud

    What kind of cable is this. What kind of circuit is this. What is the voltage. Sounds like a 240 circuit to a sub panel. What kind and size is the breaker. The maximum amperage on #8 Romex is 40 amps. Maximum amperage on #6 Romex is 55 amps.

    No, you cannot splice on #6 to #8 and use it like #6 wire.
    Better tell us what you are doing.


    Delete all of you other post. Put everything in one post. We can't keep track of you.
  • May 16, 2010, 08:26 AM
    donf


    Did anyone notice that according to the poster, he is running 55 amps on #8 cable instead of #6. No wonder the cable is getting hot, it's the wrong size.

    Questions:

    Are you in a mobile home?

    Have you ever had an electrician correctly size this feeder to make sure you have the proper size feeder for the calculated load?

    What is the size of your incoming service from the Power Company?

    Is this a feeder to a sub panel?

    Please give a complete description of the cable you are using, particularly the temp rating and type of insulation on the cable.

    While #8, conductors can carry 55 amps, in the 90 (C) column that does not apply, unless the entire circuit is constructed using 90(C) components.

    60 (C) and 75 (C) are commonly tested and listed as residential components.
  • May 16, 2010, 09:12 AM
    Missouri Bound
    Theis poster is looking for an answer he agrees with. Unfortunately unless the situation is corrected very soon, he's likely to experience a total electrical failure, and the worse case is a fire. A professional needs to be called in immediately and get this resolved before any personal or property harm happens. He's playing Russian roulette with his life.
  • May 16, 2010, 04:03 PM
    rottenrichard00

    I am not sure how to work this thing. If I splice it what will happen? I don't know if you noticed but I live in Mexico, so we can get away with something, but I still want to get it right.
    The last 2-3 ft going into the meter is in solid cement I cannot get to it, and I don't want to change the whole meter unless I have to.
  • May 16, 2010, 04:07 PM
    rottenrichard00

    Cable Indiana THW-LS/THHW-LS ANTIFLAME 8.37MM 8AWG 600V 75/90 VW-1 ANCE. 50ft yes 240 to a sub
  • May 16, 2010, 04:07 PM
    rottenrichard00

    What is the temp on the wire for 75/90 ?
  • May 16, 2010, 04:13 PM
    rottenrichard00
    Quote:

    Originally Posted by hkstroud View Post
    What kind of cable is this. What kind of circuit is this. What is the voltage. Sounds like a 240 circuit to a sub panel. What kind and size is the breaker. The maximum amperage on #8 Romex is 40 amps. Maximum amperage on #6 Romex is 55 amps.

    No, you cannot splice on #6 to #8 and use it like #6 wire.
    Better tell us what you are doing.


    Delete all of you other post. Put everything in one post. We can't keep track of you.

    #8 stranded, no romex 3 wires -2#8 1#10 cables to a 100 amp sub. Sound like I need #6 at least mabie #4 ? Breakers can be changed no problem, the only thing I can not change is the last 2-3 ft is in solid cement.
  • May 16, 2010, 06:12 PM
    donf

    Okay, you are officially scaring me.

    The length of cable that passes through concrete, is it in conduit?

    If I read one of your responses, you are using only 240 VAC. None of the connections at the sub panel will need 120 VAC?
  • May 16, 2010, 06:48 PM
    rottenrichard00
    Quote:

    Originally Posted by Missouri Bound View Post
    Theis poster is looking for an answer he agrees with. Unfortunately unless the situation is corrected very soon, he's likely to experience a total electrical failure, and the worse case is a fire. A professional needs to be called in immediately and get this resolved before any personal or property harm happens. He's playing Russian roulette with his life.

    I live in Mexico, I am probably the most qualifyed with in 1000 miles, there is no danger because I can select what to turn on or off, until I fighre this out I am keeping two of my A/C's off. I checked the wireing to day with the two A/C's off and the wires were normal room temp. what is the temp on the side of my wire it said: Indiana THW-LS/THHW-LS ANITIFLAME 8.37 mm 8 AWG 600v 75c/90c VW-1 ANCE, MY MAIN is 100Amps, the sub-panel is rated at 100amp max, 50ft -2#8-1#10. Looks like I need 2#6-1#8 ?
  • May 16, 2010, 07:22 PM
    Stratmando

    If you are planning for growth and/or have the money, how about #4's(100 amp).
    Motors and Compressors hate Low Voltage.