I have a problem where my heat pump contactor isn't pulling it. It's a 17 year old W
I have a problem where my heat pump contactor isn't pulling it. It's a 17 year old Weatherking unit. I saw that I was getting some voltage at the coil so I replaced the contactor. It still didn't pull in, so I checked the voltage again and then I noticed that I was actually getting ~14.5V on both sides of the coil, not 24v. I checked the R & C contact points in the thermostat and verified that I have 24V there. If I manually press in the contactor, the compressor and fan run. What would cause a voltage drop like that? I know there's a transformer at the air handler, that I assume provides the 24V to the thermostat. I assumed that the thermostat then sends the 24v to the coil when calling for cooling. I did notice a second transformer in the outdoor unit, that leads to a control board. This control board does have a wire leading to one side of the contactor coil. Could that transformer be the problem?