The LRA is seems to be more than 100amps on these current why don't the olp disconnects the circuite?
![]() |
The LRA is seems to be more than 100amps on these current why don't the olp disconnects the circuite?
Missing info like breaker size. I'm assuming 60A.
LRA is Locked Rotor Amps Breaker won't see that current unless the compressor motor (internal) isn't moving.