S-Trap or not? Also Venting issue.
After much planning, Questions, and Answers I installed the drainage plumbing in my home. I had our local mechanical inspector over and he was happy with everything upstairs however when he looked downstairs he was concerned. The first thing he said was that I should have hired a professional plumber. Then he said the drainage from the shower is an illegal S trap and that it needs a vent.
He proceeded to say that the toilet drainage needs a vent as well.
The 2" drain on the shower runs 5" Horizontally after the P trap (more than double the diameter of the pipe) before the 90 going down. The total length of pipe is about 2' before it goes into the stack.
The 3" Toilet drain runs only 5' before it hits the main stack.
From what I know the rule of thumb for S traps is to make the horizontal distance no less than twice the diameter of the pipe.
The critical venting distance for 2" pipe is 5'.
The critical venting distance for 3" pipe is 10.
Are these applicable rules in my case?