    The furnace will run for 3 min then the relay kicks out
    I have repalced the nozzol and the fliter at the tank the way it look like it was never changed... so if I hold the reset button down it will fir up and run for like 3 minutes then it just kicks out and the red light comes on... I have bleed the air out so that's not the problme and this is the same problme from the begging of trying this stuff plase help if possible
  • Apr 16, 2010, 06:36 AM
    Joshdta

    Could be air getting in, check the nut at the filter. Or could be a dirty cad cell, try wiping it off with a rag.
  • Apr 16, 2010, 07:35 AM
    4322558

    Joshdta thanks I cleand the cad cell and its been running fine so far thanks agine
  • Apr 16, 2010, 08:21 AM
    4322558

    So the cell hardly ever goses if so how much do they run ? Thanks agine
  • Apr 16, 2010, 08:25 AM
    Joshdta

    They normally don't go bad to often, just need to be cleaned. Looking at the book here says between $19.75 for the one kit and $25.72 for the other.
  • Apr 16, 2010, 12:11 PM
    4322558

    Well it just lock out agine... mybe the cad cell is bad ? Because it ran a lot longer then it did the frist time after cleaning it
  • Apr 17, 2010, 07:44 PM
    4322558

    I clean the cell agine and its been running fine knock on wood