    240/120 volt single phase (80 amp load) underground 180 feet
    What is the recommended wire size to allow the use of either 2 hp radial arm saw or a stick welder plus 20 amp continuous lighting load.
  • Apr 15, 2010, 04:02 AM
    stanfortyman

    I'd go 1/0al or #3cu.