  • Apr 13, 2010, 11:33 AM
    karmakore
    3 prong 240 volt dryer outlet
    While testing my 3 prong 240 volt dryer outlet I get 240 volts off the two "hot" leads but only 63 volts when individually testing a single "hot" lead with the neutral.
  • Apr 13, 2010, 01:21 PM
    tkrussell
    Could be a broken or open neutral. Need to check all connections in this circuit, from the receptacle back to and including in the panel.
  • Apr 13, 2010, 04:08 PM
    karmakore

    I have checked the power at the panel and everything checks out 240v on both hot leads and 120v on each leg when checked with neutral. So I will need to trace the neutral ?