  • Apr 6, 2010, 07:32 AM
    alsmith123
    Trouble shooting carrier heat pump
    Ac or heat pump will not come on when I reset the breaker it makes a humming noise about one second and then does nothing. It's a carrier 4 ton unit the unit is 12 years old the breaker does not trip. The fan does not come on either on the outside unit. The air handler is fine.
  • Apr 6, 2010, 05:09 PM
    Joshdta

    Sounds like the duel start capacitor has went bad.
  • Apr 7, 2010, 05:43 AM
    alsmith123
    Quote:

    Originally Posted by Joshdta View Post
    sounds like the duel start capacitor has went bad.

    You are 100% right Thanks my friend..