Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Goodman gmp050-3 Burner Shuts Off before heating (https://www.askmehelpdesk.com/showthread.php?t=462241)

  • Apr 3, 2010, 10:40 AM
    kgreen812
    Goodman gmp050-3 Burner Shuts Off before heating
    The furnace control board went bad and has been replaced. The new issue... it will not stay burning through a heating cycle: 1. thermostat calls for heat. 2 induced draft blower starts. 3 ignitor activates. 4 audible click, gas introduced with light off... burns for 1-2 seconds(indoor blower begins its cycle) followed by audible click and gas shut off. 5 induced draft blower shuts down. 6 Then the same cycle restarst again.
  • Apr 3, 2010, 02:31 PM
    Joshdta

    Drity flame sencer and too much gas pressure will cause this
  • Apr 6, 2010, 11:33 AM
    kgreen812

    In addition, there is 24 volts when gas is called for, within 1 second the power is cut and gas flow is interupted.
  • Apr 6, 2010, 03:21 PM
    mygirlsdad77

    As Josh mentioned, I would start by cleaning the flame senser