    Tempstar Furnace tripping rollout switch
    Hi,

    This just started last night. Furnace would blow cold air and the only way to shut it off was to hit the main switch on the furnace.

    After some research I found that the rollout switch was tripped. I reset it and it worked for 1 cycle. Upon starting back up it tripped again. Just tried again and it tripped in 3 minutes or so.

    Do you think the switch is bad? What else could it be. The filter is brand new,it is pvc vented out the side of the house.

    Tempstar Model-NTG9075FGA2

    Thanks
  • Mar 27, 2010, 06:07 PM
    Joshdta

    Does the flame start to flutter when the fan comes on?
  • Mar 27, 2010, 06:59 PM
    maximusprime
    Quote:

    Originally Posted by Joshdta View Post
    Does the flame start to flutter when the fan comes on??

    Yes, I did notice a little flutter/ saw some evidence of an orange flame.
  • Mar 28, 2010, 12:43 AM
    Joshdta

    Sounds like you may have a cracked heat exchanger, or stopped up secondary heat exchanger.