I have run a sub feed to a 125 amp panel with 1/0 aluminum ser cable, 400 ft. This is a 120/208 volt single phase application. Is this o.k.
![]() |
I have run a sub feed to a 125 amp panel with 1/0 aluminum ser cable, 400 ft. This is a 120/208 volt single phase application. Is this o.k.
What is the calculated load in amps? Voltage drop calcs require the amps to complete.