    Central heating water level
    I can't understand why water keeps coming from overflow on my headder tank .
    I have turned tap which fills tank OFF . When heating is on the level DROPS but then rises again once the water in system cools... can't understant this, I expect the reverse as hot water EXPANDS so would think it should rise when hot...
    Can anyone expand on this.. Is it that I have leak in coil inside hot storage tank?
  • Nov 30, 2006, 03:47 PM
    caibuadday
    Quote:

    Originally Posted by eddiescars
    i can't understand why water keeps coming from overflow on my headder tank .
    I have turned tap which fills tank OFF . when heating is on the level DROPS but then rises again once the water in system cools...... can't understant this, I expect the reverse as hot water EXPANDS so would think it should rise when hot.......
    can anyone expand on this...... ? is it that I have leak in coil inside hot storage tank ??

    The" fill tank", make up, could be leaking by, yes the coil in the storage tank may have a hole in it... shut off the IN/ OUt valves of the storage tank to verify if it leak. It could be one of the two or both are leaking
  • Nov 30, 2006, 07:17 PM
    NorthernHeat
    That is odd, my first look would be at the expansion tank.