-   -   Is a #8 cable adequate for a 50 Amp service to double wall ovens? (https://www.askmehelpdesk.com/showthread.php?t=456610)

  • Mar 10, 2010, 11:21 AM
    giljoy89
    Is a #8 cable adequate for a 50 Amp service to double wall ovens?
    I am replacing 24" double wall oven with a new 30" double wall oven. I know I will have to up my 40 Amp circuit breaker to 50 Amps, but Do I have to replace the wiring too? Presently the cable to the ovens has a #8 on it for 8 gauge. Is this OK?
  • Mar 10, 2010, 01:49 PM
    tkrussell
    #8 copper NM-B, or Romex, is only rated 40 Amps, #8 copper MC cable is rated 50 Amps. If you want or need to use Romex, you will need #6 copper.