    Bonding neutral in a transformer
    If you bond your neutral in a transformerdo have to bond your neutral in a panel.
  • Mar 9, 2010, 06:05 PM
    tkrussell
    No, either at the panel or at the transformer. Typically it is done at the transformer, along with the grounding electrode conductor that connects to building steel or any other approved grounding electrode.