-   -   Replace a Lennox T834C1475 with a Honeywell TH4110D (https://www.askmehelpdesk.com/showthread.php?t=455135)

  • Mar 6, 2010, 04:48 PM
    revtogo
    Replace a Lennox T834C1475 with a Honeywell TH4110D
    The Lennox T834C1475 themostat has four wires but the Honeywell TH4110D seems to require five wires - what do I need to do to fit the Honeywell
  • Mar 6, 2010, 08:33 PM
    letmetellu

    If the honeywell thermostat is a battery operated thermostat you should be able to make it work with only four wires.

    The gerenaly accepted wiring at the thermostat is:

    Red wire on the Rh terminal

    White wire on the W terminal

    Green wire on the G terminal

    Yellow on the Y terminal.

    The Rc terminal should have jumper already installed to the Rh terminal.

    Now your colors may not match the colors I gave you, if they don't you neet to go to your furnace or air handler and look at the low voltage area of the circuit board and see how the colors are matched there and then do the same at the thermostat.