  • Mar 2, 2010, 03:10 PM
    vikkaraja
    Relocating sub panel 120/208 4 wire.
    Can I use a junction box to splice my feeder wires. I would like to see if code allow that. And if the code says I can not do that what are my options beside running a new set of wires. Can you please help?

    Thank you.
  • Mar 2, 2010, 06:09 PM
    tkrussell
    Sure, just that the box needs to be accessible. A min of 8x8x6 for #2 - 4 wire cable should be fine.
  • Mar 2, 2010, 07:07 PM
    donf

    Aren't you required to have the permission of the Utility company and the LAHJ prior to moving the Main Panel anywhere?
  • Mar 4, 2010, 08:21 AM
    vikkaraja

    Thank you both. Can you direct me to the NEC code for future refernace?
    Thanks again.
  • Mar 4, 2010, 08:28 AM
    tkrussell
    See Sticky for link to on line NEC, for review only:

    https://www.askmehelpdesk.com/electr...ne-270277.html