    dhawkbb
    How to wire single phase 208 wiring
    I need to power up a unit requiring 230 VAC single phase. The lab power is 230/3 phase and standard 120 VAC single. What is the correct way to wire this?
  • Mar 1, 2010, 10:20 AM
    tkrussell
    If the unit you need to connect can handle 230 volts, then all you need to install is a two pole circuit breaker into the 3 phase panel, and install your circuit.

    If your unit cannot handle the 230 volts, then you will need a buck-boost transformer rated to handle the KVA load of your unit.