Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   How do you check the gas valve coil (https://www.askmehelpdesk.com/showthread.php?t=449431)

  • Feb 20, 2010, 12:22 PM
    volk43
    How do you check the gas valve coil
    How do you check the coil in gas valve. How many ohms should it have?
  • Feb 20, 2010, 01:28 PM
    hixton

    The exact ohms vary from unit to unit check to see that you have a resistance and that its not grounded
  • Feb 20, 2010, 01:59 PM
    letmetellu

    You need a volt/ohm meter. You can unplug the furnace and use the ohm meter to check from one terminal one top of the furnace to the other. If the needle moves more that likely you gas valve is good. Another check would be to turn the thermostat up trying to get the furnace to light. While trying to get it to light hold the two leads on the terminals of the gas valve. Hold them there for several minutes, if after a couple of minutes you get 24 volts but the gas does not come on then the gas valve is bad.

  • All times are GMT -7. The time now is 04:19 PM.