  • Feb 17, 2010, 10:28 AM
    jureidii
    The blower doesn't start on
    My furnace Lennox G20Q3/4E-100-5 behaves as follows:
    1) Fan is on "Auto"
    2) Thermostat calls for heat
    3) Flame occurs
    4) Blower doesn't come "On". After a while, the burner stops due to safety. It retries again, and same thing happens.
    5) When the burner is "On", I put the blower on "Fan On" mode and the furnace keeps running until it meets the thermostat set-point. Then the burner goes "Off".
    Blower keeps running, because it's on "Fan On" forced mode.

    I see where someone had same problem just need to know where can I purchase the controller board or even the relays for the board would be even better.

    My location Toronto Canada.
  • Feb 17, 2010, 01:41 PM
    hvac1000
    You have a fan control problem in the auto mode.

    Here is your service manual. Looks like it is a board problem.

    http://0190acd.netsolhost.com/manuals/G20_Series.pdf
  • Feb 17, 2010, 06:18 PM
    jureidii

    I figured it was the controller board I'm trying to find similar boards (defective) that I could scavenge some parts such as a relay to see if that resolve the issue. The furnace did this once before but started working again after I had set the thermostat to a much higher temperature.