    danarh
    What is the wire size for a 30amp circuit at 200 feet?
    I am trying to install a 30amp sub-panel out to my barn from the house. The wire run is approximately 200 feet including the internal wire distance in both buildings. What wire size do I need to use? Will 8/3 with ground be sufficient?
  • Feb 17, 2010, 05:08 AM
    tkrussell

    #4 copper will be needed to deliver 30 amps 120 volts 200 feet.
  • Feb 17, 2010, 05:33 AM
    danarh

    My oversight... sorry. 30 amps 240V at 200 feet. What is the required wire size?
  • Feb 17, 2010, 05:45 AM
    tkrussell
    #6