OK here goes. This week I installed a 3 zone system on an existing furnace using a Robertshaw Simline Classic zone control(I've used this dozens of times with great success).
All went well until the customer called me and said that the furnace was overshooting the t-stat by 2 or 3 degrees.This was unusual. I spent a couple of hrs observing and was surprised to see a 4-5 min fire after the t-stat was satisfied.(I jumped R & W, fired the burners, removed the jumper... gasvalve remained open). I called York tech support and was told that it was either a sticky gas valve or faulty board. Tested the gasvalve, OK. Board is doing everything as asked so it seems OK.(I don't always trust Tech support but that's another story)
After further online research I fount this info @ Johnston controls{York}:
"York MODELS: PC9*DH
UNLIKE CONVENTIONAL SYSTEMS, THE
WALL THERMOSTAT DOES NOT SIMPLY TURN THE FURNACE ON
AND OFF. THE FURNACE CONTROL CALCULATES THE DEMAND
AND MAY CONTINUE TO FIRE THE FURNACE DURING PORTIONS
OF THE THERMOSTAT "OFF" CYCLE"
I said to myself "what the heck" now I have a perfectly good zone system and a perfectly good furnace that won't co-operate.
Any suggestions as to how to remedy the problem?