Attached garage sub panel wire type and size
Hello
I am getting down to wiring the garage now for lights plugs and 50amp welder.
In earlier posts I received a lot of well appreciated information on my 100 amp sub panel in the basement taken from the tap box I installed above the 200 amp main disconnect.
Thanks again to Tkrussell, Washington1 and others that have contributed.
By the way Tk your Pink Floyd "Dark side of the moon" logo brings back some old memories. It would make interesting music for wiring up a job lol.
Originally I was going to run all the wires out to the garage from the 100 amp sub panel but I am thinking it may be better and more convenient to just run one wire out into the garage to a 100 amp sub. That will give me mush less wires going through the chase along the back side of the basement ceiling and also allow me to have access to the breakers right in the garage. It will also allow me to keep a few breakers free in the new 100 amp sub in the back left end of the basement as it is filling up fast with the surge arrester ,arc fault,ground fault and double pole breakers as well as the circuits that need to be on separate breakers. The sub panel to the garage will save me from having to use an twin or quad breakers in the new Siemens 100 amp sub panel. The panel states it can use the twins and quads throughout the panel but from the feedback I have received from my other post most of the electricians seem to frown on using the twins and quads mostly because of possible overheating issues of the breaker and panel bus connection. I haven't found any solid data on failure of these breakers to support these claims though but a margin for safety is always a good idea. The twins and quads seem to be a good idea too lol.
So I believe I have only one choice as a start point for the circuit and that is at the tap box. I can't see putting a 100 amp breaker with in the new 100amp sub that has it's own 100 amp main breaker as that just doesn't seem to make sense.
Ok if I go this route then I would proceed as follows,
1. Take out the permit (Keeps Ontario Hydro happy!)
2. Install sub panel on garage/basement wall about 1/3 from back of garage.
3. Install 100 amp disconnect beside panel.
4. Run my circuits from the sub panel for welder,lights, wall plugs,central vac,sub pump,heater circuit and exterior garage GFIC plugs etc.
5. Run feeder wire from tap box to 100 amp disconnect in garage. Connect feeder ground to tap box panel ground and main disconnect panel ground.
6. Run feeder wires from 100 Amp disconnect to 100 amp sub panel as well as feeder ground wire from disconnect panel to sub panel. Keep all grounds separate from the isolated common connectors.
7. Call in inspection and if all good flip the disconnect switch with eyes closed and fingers crossed behind back.
My main question is does this seem like a logical way to go and if so what size wire would be best for the feeder?
Our code book here in Ontario states for 100 amp you will need
2- #3 R90XLPE black,red or blue for the hot
1-#3 R90XLPE white for the neutral
1-#6 copper for the ground wire
All these wires should be in 1 1/4" conduit.
Can I run insulated #2-3 wire plus ground copper cable without a conduit through the ceiling chase in the back of the basement? The reason why I ask this is there is a length of it over at the habitat for humanity store that is in good condition and the right length for around $75.
Do I have the disconnect in the right place and is it a problem having more than one new sub panel?