  • Feb 11, 2010, 04:32 PM
    mikestice
    Intertherm furnaces
    My motor on this intertherm circa 1988 vintage, runs slow. I just replaced it. Before I replaced it the motor never started. I could spin it and maybe it might start. Now I have what I consider to be the original problem back... what might be causing this. I have voltage at my burnbox sensors and when the limit trips the motor begins to spin. However, it spins like it is running only on 110, and not 220 VAC.

    What could be going on here? Thank you in advance...
  • Feb 11, 2010, 06:56 PM
    hvac1000
    Did you replace the old motor capacitor with a new one sized for the new motor.
  • Feb 11, 2010, 08:27 PM
    johnair77

    Check voltage going to the mtr. is it 120volts?
  • Feb 12, 2010, 08:54 AM
    mikestice
    I have 120 at the motor, yes I change the run cap... found a bad ground connection which when tightened produced the desired heating effects through fan motion. Thank you... sometimes a person just needs to be patient when changing large components out...

    Michael.
  • Feb 12, 2010, 08:56 AM
    mikestice

    I believe 32 years is a good age for a motor to die, what do you think?
  • Feb 12, 2010, 09:26 AM
    KC13
    Quote:

    Originally Posted by mikestice View Post
    I believe 32 years is a good age for a motor to die, what do you think?

    Nah, they should last FO-EV-AH! :D Most furnaces don't last that long.