Quad breaker usage and safety
Hi Folks
I have a situation where I would like to run the kitchen plugs in my basement reno summer kitchen. Our Canadian code book here for Ontario (Ontario Electrical Code Safety Code) changes like the seasons. Now we can wire the outlets three different ways. These are as follows
15 amp split receptacles with no two outlets side by side. Using 15 amp wire (14/3)
And 2-pole breaker with tiebar
20 amp non split receptacles with max two outlets not side by side on same circuit. Using 20 amp wire (12/2) and 20 amp receptacles.
20 amp non split receptacles with one outlet per circuit. Using 20 amp wire (12/2) and 20 amp receptacles.
Outlets beside the kitchen sink must be GFCI now as well.
The code book states for the third option you can run a 12/3 wire to the first receptacle and then branch a 12/2 wire to the second receptacle for two 20 amp circuits using 2-20 amp breakers.
My first question using the 12/3 wire should or can you use a 20 amp 2-pole breaker with the tiebar (normally used for 240v load) to run the 12/3 dual circuit or should you use 2 separate 20 amp single pole breakers. I understand if you used the 20 amp double pole with the tiebar then both circuits would pop off at the same time but would that be safer than having someone doing electrical work on the outlet box with the 12/3 to 12/2 branch pass through to make sure power is shut off in the complete outlet not just on one wire of the 12/3 branch.
The second question is I am running out of space quickly on the new 100 amp sub panel with 32 circuits (scary) due too a lot of the breakers taking up two spaces (surge protector breaker, 240 breakers and all those little things that seem to take up breaker space) I had this setup shown on an earlier post regarding sub panels. I do have space in the distribution box to tap in more 60 or 100 amp wires but I was trying to avoid any additional panels other than the possibility of running a 6/3 welder wire to a 50 amp breaker in a small sub panel.
So my thinking is I would like to use a few Siemens Quad breakers to save room in the new 100 amp 32 circuit panel. The possible combinations vary but as an example 15/15-15/15 , 15/20-20/15, 15/30-30/15, 15/15/15/15 . The first three have the middle 2-poles ties for 240v circuits such as heaters, air conditioner etc.
Are these breakers safe as I understand the middle two poles share the panel connection to the bus with the outer breakers. Can they be safely used for baseboard heater,water heater,stove loads without overheating the breaker?
Also the code book doesn't specify whether to use 2 separate single pole breakers for the 12/3 wire for the kitchen receptacle dual circuit discussed above. I have a 15/20-20/15 quad (Siemens Q21520CTNC) with the middle two breakers being 2 pole common trip as they have the tie bar. Can I use the middle 2-pole to connect the 12/3 wire for the two 20 amp 120v kitchen plug non split receptacle circuits? Red wire to one pole and black to the other pole and white to common. I think that still balances the load on the common. It would be similar to connecting a 15 amp split receptacle circuit breaker. The code book states that the 3-wire circuit in this situation does not need to be two pole but the breakers need to be adjacent. It does not state that you can't use a 2-pole breaker with the tiebar. Or do you feel the electrical inspector may have an issue here?
Home Depot description of quad breaker,
If you're doing a renovation and find that your breaker box is running out of room, use this space-saver to double your circuits. Simply replace a single pole 15 Amp breaker and a two pole 20 Amp breaker with this one to expand it into two 15 Amp single pole circuits and a two pole 20 Amp circuit. Each 15 Amp circuit could be used for general 110V applications such as lighting and receptacles and the 20Amp could be used for an air conditioner or a heater.
Wow next house I may go with a 400 amp service instead of the 200 amp service. It is scary how fast you can fill a new sub panel up. The breaker spaces in the upstairs FPE Stab lock panel are full now with the new addition wired in. The new Siemens panel sure looked good before I started filling it. The new panel is taking a few new circuits from upstairs as well (easy to wire under the floor than in the attic) Maybe I should run a 100 amp sub from tap box to the basement garage to free up some circuits? I haven't completed the wiring to the new panel yet and the garage circuits still have to be run. I assume that because the garage is in the same building as the main power that I can use the main ground connection in the tap box. The 200 amp main disconnect switch is below the tap box. Most of the basement will just be used part time.
Thanks very much for any input.