Please purchase a Volt/Ohm meter so we can isolate switch loops from feed conductors.
It sounds like the Breaker feed is coming into the ceiling box. You should find one set of Black and White conductors that is "Hot". With the red probe from the meter on the Black conductor and the Black probe on the White conductor, you should see approximately 123 VAC.
Once you find that pair, turn the power off at the breaker and isolate the cable or Black/White conductors. Now set the meter for Ohms 1K value.
Now for the switches. Separate the remaining two pairs. Set the meter to Ohms (1K). Place the red probe on the Black conductor. Place the black probe on the White conductor. Check the meter, do you see zero (0) ohms or an open circuit?
If you now go to a switch, and move the handle, does the meter change?
I have only 2 sets of wires (not 3) coming out of the ceiling box and I am replacing a ceiling fan with a Flush Mount Ceiling Light. I identified the live wires and connected them to the light fixture wires - black to black and white to white; light doesn't work. What else is needed?