    Nordyne Propane Furnace - no heat
    I have a Propane furnace model # KG6RC-060C-12A. The furnace fires up but shuts off after a few seconds. It attempts this 3 times and then shuts off. The code light is blinking 4 times. I checked the wiring for loose grounds and it appears to be OK. The unit is only 3 years old. Any suggestions on what it could be or how I should proceed?
  • Feb 1, 2010, 10:07 AM
    realredwood
    Nordyne Propane Furnace
    I have a Propane furnace model # KG6RC-060C-12A. The furnace fires up but shuts off after a few seconds. It attempts this 3 times and then shuts off. The light is blinking 4 times. I checked the wiring for loose grounds and it appears to be OK. The unit is only 3 years old. Any suggestions on what it could be or how I should proceed?
  • Feb 1, 2010, 10:35 AM
    hvac1000
    2 Attachment(s)
    Try cleaning the flame sensor with fine sandpaper or steel wool.
  • Oct 20, 2011, 05:38 AM
    Dennisjr
    Red light
    On = Power
    1 Flash = Limit Circuit Open or External Load on "W"
    2 Flashes = Pressure Switch is Open with Inducer ON
    3 Flashes = Pressure Switch is Closed with Inducer OFF
    4 Ignition Failure( Check ground)
    Continuous blink= False Flame or Gas Valve Relay Shorted

    Yellow Light
    On= Flame Present
    Continuous flash= Low Flame Sensor Signal