  • Jan 29, 2010, 04:48 PM
    allen87
    Goodman furnace will not shut off when both wires are disconnected
    Goodman furnace will not shut off when both wires are disconnected
  • Jan 29, 2010, 04:49 PM
    allen87

    Goodman furnace will not shut off when both wires are disconnected from thermostat
  • Jan 29, 2010, 05:21 PM
    allen87
    Goodman furnace
    I have replaced the thermostat and the furnace continues to run. I can disconnect both the red and white wire from the thermostat and the furnace still will not shut off
  • Jan 29, 2010, 05:22 PM
    mygirlsdad77

    Hi allen.

    Are the burners still burning, or is just the fan running? Is the unit heating the house good, or is it not keeping up to temp?
  • Jan 29, 2010, 05:23 PM
    allen87

    What can be done? The furnace is only 5 years old
  • Jan 29, 2010, 05:26 PM
    mygirlsdad77

    Please stick to just one post per question. You will get better help this way. We need to know if the burners are lit, or if just the fan is blowing.
  • Jan 29, 2010, 05:26 PM
    allen87
    Goodman furnace will not shut off after replacing the thermostat
    I replaced the thermostat and the furnace continues to run. I can disconnect the red and the white wire and the furnace continues to run
  • Jan 29, 2010, 05:34 PM
    allen87

    The burners are lite
  • Jan 29, 2010, 05:38 PM
    wmproop
    Sounds like you replaced the tstat for nothing, take the tstat wires loose at the furnace, if it stops working after you replace the door, you will no there is a shorted tstat wire
  • Jan 29, 2010, 05:39 PM
    mygirlsdad77

    Allen. Disconnect the red and white wires at the furnace control board. This will tell me if the wires are shorted between the furnace and the thermostat. Let me know what happens when the red and white are disconnected at the furnace.
  • Jan 29, 2010, 05:39 PM
    wmproop
    Sounds like you replaced the tstat for nothing, take the tstat wires loose at the furnace, if it stops working after you replace the door, you will no there is a shorted tstat wire


    Double your pleasure, double you fun, with doublement gum
    https://www.askmehelpdesk.com/images/misc/progress.gif
  • Jan 29, 2010, 05:39 PM
    mygirlsdad77
    You beat me to it wmproop
  • Jan 29, 2010, 05:41 PM
    wmproop
    Lol,, great minds work alike
  • Jan 29, 2010, 05:43 PM
    mygirlsdad77

    That's right