			You are correct, you will not want to pul SER cable thru conduit.
 
You can use 3- #2 Al XHHW and 1 # AL XHHW pulled thru the conduit.
 
AFCI must be used to protect all 120 volt outlets (the word "outlets" means all receptacles, lighting fixtures, and smoke detectors) located in, and I quote from the 2008 NEC:
 
"family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms, or areas".
 
GFI protection covers the remaining areas of a home, such as kitchens, bathrooms, unfinished basements, garages.
 
Would be good to consult with your local city or state code for changes or waivers to the national electric code.