    No heat from a Coleman Direct vent forced air furnace Model #7680a
    I am having promblems with getting the heat from an older Coleman Direct vent forced air furnace Model #7680a that's installed in a mobile home. The thermostat was replaced The fan comes on. The pilot feed that goes into the side but isn't attached. Do u have any specs on this model?
  • Jan 28, 2010, 08:59 PM
    hvac1000
    No but I know a site that specializes in Mobile home furnaces especially Coleman. Go to the link below sign in and post your question under Coleman.

    Index page
  • Jan 28, 2010, 09:16 PM
    Geokohler

    First reattach the feedline to the pilot light. You need to hold down the control until it lights and continue to hold it for a while to allow the thermocouple to heat up and allow gas to flow. You may need a long wire with a match twisted to the end to light it. They didn't place it in the best location.

    Next Check your upper and lower limit switches these are the proper settings:
    Upper = 7680-3791= Open @ 140*/Close @ 120*

    Lower = 7660-3591 = Open @ 150*/Close @ 130*

    Fan- Limit = 7700-3281 = Open @ 120*/Close @ 90*

    Next check the burner & automatic relight burner assembly, make sure they are clean and functioning as designed.

    If it still does not work feel free to contact me. George