    Tempstar furnace with fan running constantly
    I have a Tempstar NTC6050FBG1 gas furnace with the blower running constantly. Should the terminals on the board for the fan on cool and heat have 110v when calling?
  • Jan 27, 2010, 08:36 AM
    johnair77

    If blower running you will have voltage on the heat or cool terminals unless unit is miswired.. check to see if you have a limit open, these will cause blower to run continuous are some models.