    Wired Smoke Detectors
    Rewiring old house to code. Notice that most (if not all) wired smoke detectors have a base plate that the main unit attaches to, mounted to ceiling/wall with 14/3 wire dropping through middle. Generally speaking, for rough inspection purposes, is it best to plan to mount the base plate to a can, allowing for the inspector to see the drop in some type of container instead of just hanging there stapled and waiting for celiling to go in or (where ceiling still exists) hanging out of a hole?
  • Jan 25, 2010, 09:20 AM
    tkrussell
    Smoke detector wiring is 120 volts, and each smoke detetor needs to attached to an outlet box containing that wiring and splices.

    For rough in purposes, all outlet boxes are to be installed, and all cables spliced in the outlet boxes. The mounting ring of the detector does not need to be installed on the box, until trim and finish is done.
  • Jan 25, 2010, 09:24 AM
    glilley

    Tkrussel - Thanks! That's what I figured and its good to have it confirmed.