Hello all,
I'm a software engineer and am in the process of setting up a server rack in my home to serve as a lab for my work. The rack will hold 6 server grade computers, 4 regular PC's, and some other network related equipment.
I have 100 amp service into my home now, which I'm upgrading to 200 amp service tomorrow. I'm having a professional electrician do the work. During the bidding process, I told each electrician why I needed to upgrade to 200 amp service. I even showed them the servers which will be consuming so much power. I pulled out one of the power supplies to one server, and it reads like this:
AC INPUT
100-127V~,50/60Hz,8.3A
200-240V~,50/60Hz,4.0A
DC INPUT
140-224V,5.5A
DC OUTPUT
12.2 V 48 A
5 Vco 0.2 A
TOTAL 585W MAX
Five servers each have one of these power supplies. One server has three of these power supplies.
One electrician looked at a power supply and simply added up the 8.3 amps as described in the specs above, and came up with approximately 64 amps (~8A x 8 power supplies). He said because these servers will be on constantly, we'll need to dedicate the additional 100 amp service just to the rack of servers.
This made some sense to me, but of course I'm not an electrician. But, in the grand scheme of things, this no longer is making much sense to me. Because I've had several of these servers running on a single 20 amp circuit, along with 2 large monitors, an aquarium (pump, water heater, large bulb), 2 laptops, and several other network devices, and the circuit never failed. So, I'm confused about why I need a whole whopping 100 amp sub-panel installed next to my rack of servers.
Besides, ultimately I will be installing uninterruptable power supplies (UPS) in front of the servers. A UPS only has a single power cord, and between 4-8 outputs to run 4-8 servers. How do we calculate the amp's required on a single outlet that's plugged into this UPS? I don't get it.
Can someone clarify this whole capacity planning thing? I mean, from what I gather from this electrician, I'll need to run a separate circuit for each server. That's 8 separate circuits for just the 5 servers, and then a few more for the other network equipment?
Not making sense... :confused: