Existing 2 pole 15 amp breaker,14-2 wire, red, black & bare ground. Poles labeled kitchen lights and bath lights & fan. The fan has an outlet fan and a second small fan that includes a heater coil. The fan box carries a lebel 14.2 amps. The breaker pole sides seem to be misslabeled as I measure the current, the with fans running I get like 11.2 amps with the black wire in the loop ammeter in the breaker box and 0.3 amps measuring the red wire. If I switch on a kitchen light, the amps through the black wire increases and the amps through the red wire stays the same. I thought the box is wired wrong, but as I read about breakers, I think I just need to replace the 15 amp double pole with a 20 amp double pole as the fan and kitchen lights is forever blowing the 15 amp breaker.