  • Jan 19, 2010, 10:24 AM
    chirodox
    wiring a lennox cb29m
    I have a totaline P474-1050 stat, Lennox cb29m-51-1p FAU, and a lennox HP 26-042-7P heat pump. It was working fine and one morning it stopped. There is a white wire hanging free in the FAU that looks like it should be connected. My wire path goes like this:
    STAT FAU HP
    R red R red R
    G green G Green only connects stat to fau
    Y1 ------- yellow------ Y1 passes through FAU to HP
    W1 -------blue -------- O passes through FAU to HP
    W2 white White from stat hangs free in FAU looks like it should connect
    C Brown C brown C
    W1 white W1 white from HP to FAU

    We had a small earthquake ( I didn't feel it) that could have knocked a wirer loose, so I am curious if the white wire from the stat to the FAu should be connected to something.

    The totaline stat has these connections,
    G=fan
    Y1 = cooling
    W1= ,O/B heating and reversing valve
    R= power
    C= common
    Y2= 2nd stage cooling
    W2= 2nd stage heating

    there is hand written markings on the fan drum schematic: white= W2, blue = reversing valve, brown = common
  • Jan 19, 2010, 10:32 AM
    wmproop
    Guess I`ve not been around long enough,, what is a FAU?
  • Jan 19, 2010, 11:49 AM
    chirodox
    Forced air unit, the air handler
  • Jan 19, 2010, 12:48 PM
    hvac1000
    AH is the accepted term.

    See page 21 figure 15

    This is a copy of your factory AH manual

    http://www.hvacpartsshop.com/CB29M%20Series.pdf


    THis is a copy I believe for your outdoor manual.

    http://www.hvacpartsshop.com/HP29%20Series.pdf

    Keep a copy of these on your computer for future use.

    With these two manuals and the wiring diagrams you should be able to figure it out.
  • Jan 19, 2010, 06:56 PM
    chirodox
    My stat does not have the O connection. I believe that the W1 is being used for this purpose as it goes directly to the HP O terminal. I am not sure if my unit has electric heat or not. I did not install it. When I turn it on, the HP starts but nothing from the AH.

    Thanks for the manuals. I have saved and printed both.