    As stated my gas furnace will not ignite. Looked on main board no blinking lights. Everything is connected pretty firm. I can hear it blowing from the induce blower but no igniting. I hear gas coming just won't ignite. I checked the ignitor, it has some white spark residues. Seems still good. But then I notice, seems like there has been an ignitor replacement done before, there was a broken piece from an old ignitor that was laying in the bottom.

    Everything comes down to the ignitor. I can not think of anything else. Woke up this morning noticing no heat, the breaker was tripped so I flipped it back and went under to check. The above is all I can conclude so far.

    If anyone has any input please let me know. Thanks in advance.
  • Jan 14, 2010, 02:01 PM
    hvac1000
    2 Attachment(s)
    It would be nice to know why the breaker was tripped.

    Does the ignitor glow as the unit is starting up.(watch it for a minute)

    It is possible the flame sensor is dirty.
    Clean the falme sensor. Use fine sand paper or steel wool.
  • Jan 14, 2010, 03:53 PM
    oskivwj

    Don't know why the breaker tripped. Is the ignitor suppose to glow cause mine didn't. If so it must be the ignitor.
  • Jan 14, 2010, 05:11 PM
    hvac1000
    Ignitor OR the circuit board not supplying voltage to the ignitor.
  • Jan 14, 2010, 05:39 PM
    oskivwj

    Will check circuit Board to see if its working. Should be 24 volts right? If it is 24 volts I will replace ignitor. Thanks for your fast responses hvac1000.
  • Jan 14, 2010, 07:50 PM
    T-Top

    115 volts going to the ignitor.
  • Jan 14, 2010, 08:08 PM
    hvac1000
    Yep 115 is correct. If the ignitor does not light up with 115 volts going to it then the ignitor must be bad.
  • Jan 14, 2010, 08:16 PM
    oskivwj

    All right thank you fellows I'll update on how I do:)
  • Jan 20, 2010, 10:18 PM
    oskivwj

    An update... well the circuit board and pressure all seemed to check out. The ignitor was bad. I think the ignitor had a tiny crack enough to not ignite but still intact. Ordered and replaced it heater is now working like new. Thanks to all for the advise. :)
  • Jan 20, 2010, 10:59 PM
    hvac1000
    No problem.
  • Nov 27, 2010, 09:16 AM
    wookiee1978
    Furnace won't ignite, can't hear gas coming out. When it does get gas out ignites, but won't stay on full cycle. Gas coming out is a 1 in 30 tries hit and miss. Sensor clean and igniter working.