Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Industrial Products & Services (https://www.askmehelpdesk.com/forumdisplay.php?f=169)
-   -   240V 20 amp circuit breaker (https://www.askmehelpdesk.com/showthread.php?t=434192)

  • Jan 11, 2010, 02:24 PM
    bbgrell77
    240V 20 amp circuit breaker
    I'm installing 240 volt in-floor heating mats. The amperage draw is 21 amps. I intended to connect them to a 2-pole, 240 volt, 20 amp breaker. My thought was that you have two legs of 20 amp power (40 amps total). Is this correct of how the 240 volt breakers work?
  • Jan 11, 2010, 02:27 PM
    Stratmando

    Its 20 Amps total, you will need #10's and a 2 pole, 30 amp breaker.
  • Jan 11, 2010, 02:31 PM
    bbgrell77

    I was afraid of that. I think I will run two circuits since I already have a lot of 12/3 wire. The mats are in different rooms anyway. Thanks
  • Jan 11, 2010, 02:37 PM
    KISS

    For reference, since it's space heating, you multiple the current of the heaters by 1.2 and size up to next available breaker size, hence 30 A.
  • Jan 11, 2010, 02:43 PM
    Stratmando
    Quote:

    Originally Posted by bbgrell77 View Post
    I was afraid of that. I think I will run two circuits since I already have a lot of 12/3 wire. The mats are in different rooms anyway. Thanks

    How much draw and what volts for 1 heater?
  • Jan 11, 2010, 02:53 PM
    bbgrell77

    The amperage draw depends on the size of the mat. The largest one will pull 15 amps. The remaining ones are smaller and pull 6 amps combined. I'll split them into two 20 amp services which should work fine. Thanks for your input...