Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   York gas furnace troubleshooting (https://www.askmehelpdesk.com/showthread.php?t=432968)

  • Jan 8, 2010, 06:44 AM
    mnovak
    York gas furnace troubleshooting
    I have a couple of problems with my York gas furnace. First, it has a # 8 fault code which from what I understand is caused when the flame is lost 5 times. My second issue is that one of my burners is lazy and I think my heat exchanger is cracked. Does anybody have experience with that code and know of a way to confirm the crack?
  • Jan 17, 2010, 05:10 PM
    CB cooling
    First thing to check is the condition of your flame sensor. Second is what type of gas lp/natural. Third would be to check your lazy burner tube for spider web
  • Jan 17, 2010, 05:10 PM
    CB cooling
    First thing to check is the condition of your flame sensor. Second is what type of gas lp/natural. Third would be to check your lazy burner tube for spider web
  • Jan 17, 2010, 07:46 PM
    letmetellu

    There is a camera made that will go up into your heat exchanger to check for cracks or holes.
  • Jan 19, 2010, 04:20 PM
    CB cooling

    I would address the lazy flame first also if the heatexchanger is damaged the flame should move around when the indoor blower starts
  • Jan 24, 2012, 12:38 PM
    foutsbug
    I have a York Furnace, M/N LY8S080A2UH11A, 4 flashes on control board. Combustion blower runs but no ignition of gas