  • Jan 2, 2010, 08:24 AM
    tenjtenj
    Furnace is running but no air comes out of my vents
    My furnace comes on but no air comes out of the vents
  • Jan 2, 2010, 08:27 AM
    hvac1000
    If the furnace heating up? If so the blower motor or blower motor circuit is at fault.
  • Jan 2, 2010, 08:41 AM
    tenjtenj

    Furnace is on... blower is on.. air is not coming out of wall vents
  • Jan 2, 2010, 09:21 AM
    hvac1000
    If the blower is running and no air is coming out the registers it might be a belt drive blower and the belt is broked or slipping. A very dirty air filter will also cause this problem. A dirty A/C coil will also cause this problem. Anything that restricts air movement can cause this.
  • May 10, 2012, 01:03 PM
    almawal
    The professionals just installed a payne thermopomp in my house, after they left I noticed the air flow in the vents became very low, it was very strong before, what could it be, I checked all vents and all are open.