Hello;
I have a 30+ year old Rheem model RGAA forced air gas furnace that has a gas pilot light. When I set the thermostat to FAN, the fan motor turns on and runs until I switch it off. But when I set the thermostat to HEAT, either I get nothing, or the burner and motor turns on for a few minutes, then stops.
I measured the voltage across the gas valve. I read 25 volts a.c. no matter if the burners are on or off. Across the upper limit switch I read 0 volts because it remains closed. It is set to open when the supply heated air reaches 220ºF.
When I set the thermostat on HEAT and set the temperature above the room temperature, I measured zero ohms between the red and white wires at the furnace. When I set the temperature below the room temperature, I measure infinite ohms. Both readings are correct.
The only thing wrong I found was one loose plastic twist end cap that electricians use to hold multiple wire ends together. It was at the junction of power ground wires inside the furnace power kill switch box.
When I cycle the power kill switch, sometimes the burners and motor will activate for a few minutes, and sometimes nothing happens.
The pilot light looks blue and healthy and always remain lit.
I've run out of ideas and the house is getting mighty cold.
A schematic of the furnace appears at Furnace Schematic