Recently had a situation where the furnace was shutting off the gas. It was found that the flame roll out safety was activating.
Originally I thought I had a cracked heat exchange, but on inspection it was not.
Ultimately I found that there was a bee's cone in the intake restricting the fresh air.
That has since been removed.
Now I am not getting a strong flame in all the tubes causing a roll out on the flames. Any suggestions on what to look for now?