    Furnace Closet Doors
    My furnace is located in a closet next to the hot water heater. The area is closed off by 2 bi-fold slotted closet doors. This area happens to be near the living room so when the furnace runs it gets quite loud.

    I was thinking that using solid doors instead of slotted should help with the noise. However I'm unsure if that would be an issue with heat and/or ventilation of the area.

    Does anyone have some advice? I'm open to any other noise reduction tips as well.
  • Dec 28, 2009, 07:11 PM
    twinkiedooter

    Do not use a solid door as both the heater and the furnace needs air to breathe!
  • Dec 28, 2009, 08:38 PM
    letmetellu

    If you make provisions for the furnace and water heater to get fresh air you can do what you described.

    If your house is not a two story house you could run a 8 inch pipe up into the atic and down to the level of the burners on the furnace, Then do the same with the water heater with a 6 inch pipe.
  • Dec 28, 2009, 09:16 PM
    wmproop
    I`ve seen instances where the installer planned for the slotted bi-fold doors to serve as the return air,, do you have a return air system coming in from somewhere else,, some people do wild and weird things sometimes
  • Dec 29, 2009, 03:11 PM
    shaggy667

    Well there are 2 pipes going to the furnace, but I'm not sure where the ends are. I've included a picture so you can see my setup.

    Picasa Web Albums - Ben

    Also I noticed that there is a draft coming in from around the ducts as they feed up into the rest of the house. Is it safe to stuff some insulation around them?
  • Dec 29, 2009, 03:43 PM
    hvac1000
    1 Attachment(s)
    The two pipes you have now are not for combustion air, One is the furnace flue and the other is a discharge heat pipe. If you are going to put in solid doors you have to add combustion air as discussed.

    Combustion Air

    Calculator

    House of Craig - Online Combustion Air Calculator

    Providing Enough Combustion Air
  • Dec 30, 2009, 07:01 PM
    letmetellu

    One of the pipes in your picture is for the exaust fumes to leave the building through the roff. I think the other pipe is for or was for a humidifier.