-   -   Install a dryer 30 amp circuit breaker 10/2 wire (https://www.askmehelpdesk.com/showthread.php?t=428606)

  • Dec 27, 2009, 09:24 AM
    mmorr19403
    Install a dryer 30 amp circuit breaker 10/2 wire
    I recently installed a 30 amp 2 pole circuit breaker using 10/2 w/ground for a new dryer. At the box, I wired the 10/2 w/ground black to one side and the white to one side of the 30 amp 2 poled breaker and the ground to the side bar for ground.

    I also installed a three prong receptacle, wiring the black and white to each top of the "Y" and the ground to the bottom of the "Y". I ran a piece of copper wire from the recptacle box to a cold water copper pipe for grounding purposes.

    Does this sound safe or should I have used 10/3 w/ground ?
  • Dec 27, 2009, 09:46 AM
    tkrussell
    Should have used #10-3 with ground.

    Both using #10-2 and grounding to the water pipe are illegal and violates the National Electric Code.