Need a wiring diagram to connect a honeywell th3210d thermostat to goodman mbr1200aa-1 modular blower with 20kw heater coil
![]() |
Need a wiring diagram to connect a honeywell th3210d thermostat to goodman mbr1200aa-1 modular blower with 20kw heater coil
There should be a complete wiring diagram on the goodman unit. Usually located on the back of the access door.
Correct! But this isn't a conventional thermostat. Need to know where white and blue thermostat wires terminate??
Unless you have a heat pump outside you will not need the blue. The White W terminal wire is listed.
Where does the blue & white thermostat wires terminate on a honeywell TH3210D from agoodman MBR1200AA-1 modular blower with a 20KW heater element ? This isn't a conventional thermostat. Don't want to smoke the control board!!
Unless you have a heat pump outside you will not need the blue. The White W terminal wire is listed.
There is no "W" terminal on the thermostat. (E Aux Y G O L R B C )
See page 4 of the below manual for your thermostat TH3210D Honeywell. There is a connection in the manual. Read the directions for 2 heat 1 cool applications since the blower is setup for a heat pump but you only need the electric heat part. AUX or E will bring the heat on and you can connect this to the W on the goodman unit. Make sure you also go through the setup on the thermostat instructions.
http://customer.honeywell.com/techli...69-1929EFS.pdf
All times are GMT -7. The time now is 01:36 PM. |